Panel Discussion on "Service Connection"
Hosted by secretary secretary
Saturday, Sep 12, 2020 10:00 am | 2 hours | (UTC+05:30) Chennai, Kolkata, Mumbai, New Delhi
Meeting number: 170 635 1316
Password: eng!n33r
Agenda: Panel discussion on Service Connection by KSEBengineers Association
https://kseb.webex.com/kseb/j.php?MTID= ... 397743d3f7
Join by video system
Dial 1706351316@kseb.webex.com
You can also dial 210.4.202.4 and enter your meeting number.
Join by phone
+65-6703-6949 Singapore Toll
Access code: 170 635 1316
Panel discussion on Service connection for KSEBL consumers
Moderator: kunjunnips
Re: Panel discussion on Service connection for KSEBL consume
KSEBLtd submitted three cases on enhancement / reduction of contract demand.(1)Case 1:-Enhancement of contract demand, requiring replacement of the Current Transformer. KSEB Ltd stated that Current Transformers are selected considering the requirement of drawing 130% of Contracted Maximum Demand (CMD) during off peak hours. The Commission is of the considered view that the existing Current Transformer is not required to be replaced if the primary current corresponding to 130% of the enhanced contract demand is within 120 % of the rated current ofthe existingspecial class Current Transformer.(2)Case 2:-Reduction of contract demand with existing metering equipment includingspecialclass Current Transformer. KSEB Ltd submitted that if the revised load current corresponding to the revised contract demand is within 20% of full load current, the existing special class Current Transformer, is not required to be replaced. (3)Case 3:-Change in contract demand requiring replacement ofCurrent Transformer. As specified in the Central Electricity Authority (Installation and Operation of Meters)Regulations, 2006, the HT consumers shall install 0.5 S class current transformers and EHT consumer shall install 0.2 S class current transformers. If the existing current transformers in the premises of the consumer do not conform to the specificationsstipulated bythe above regulations, the existing current transformers shall be replaced.
- Attachments
-
- op92016.pdf
- Removal of difficulties encountered by HT & EHT consumers
- (347.89 KiB) Downloaded 2229 times
Re: Panel discussion on Service connection for KSEBL consume
solar off grid GBI revoking
Re: Panel discussion on Service connection for KSEBL consume
tariff order in malayalam
- Attachments
-
- tariff_revison_circular.pdf
- tariff order in malayalam
- (5.76 MiB) Downloaded 1971 times